The bathroom exhaust fan that spins but doesn't clear steam

Walked a unit last week where the bathroom fan sounded fine — motor humming, grille spinning — but the mirror stayed fogged and the paint above the shower was starting to bubble. The fan was running. It just was not moving any air out of the room.

When I checked, the grille was packed with lint, and the duct in the attic had come loose from the fan housing, so the fan was blowing moist air into the ceiling instead of outside. That is the pattern I keep finding: a fan that looks alive on a quick walk, while moisture quietly works on the paint and the drywall.

What I check now on every bathroom, before I call it good:

1. The tissue test — hold a single square of tissue to the grille with the fan on. It should pull flat and hold. If it flutters or falls, the fan is not moving air.
2. The grille — pop it off and clean the lint and dust. A clogged grille can cut airflow in half.
3. Where the air goes — the duct must run to the outside, not into the attic or a ceiling void, and it must still be connected at both ends.
4. The room after a shower — if the mirror stays fogged ten minutes after the fan has run, something in that chain is failing.

The reason it matters on inspection day is simple: trapped moisture shows up as peeling paint and mildew, and both get written up. The fan itself is a small fix. The paint and drywall it protects are not.

How do you test bath fans on your walks — tissue, hand, or something else? And what is the strangest place you have found a bath fan venting to?
 
A fan venting into the ceiling is basically relocating the bathroom problem somewhere more expensive!

The tissue test is a useful first check, but I wouldn’t treat it as proof the whole system works. You still need to confirm the duct is connected and actually terminates outside. If moisture problems continue, measuring airflow gives you more to work with than motor noise. Building America Solution Center

Did you find much moisture damage around the disconnected duct, or catch it before it got that far?
 
The disconnected duct is the important catch here. I'd use the tissue check as a quick screen, then ask for measured airflow if performance is still uncertain; it can't tell you where the extracted air ends up. The DOE ventilation guide describes checking the outdoor termination and measuring flow.

For the job record, a before-and-after reading and a note confirming the duct route would be useful. A healthy hum is a rather convincing impression of a working fan.
 
Thanks to you both — you are right, the tissue test is only a screen, not proof. It tells me the fan is pulling, not where the air ends up.

In this one we caught it early. The paint above the shower was bubbling, but the drywall underneath was still sound, so no replacement was needed. We cleaned the grille, reconnected the duct at the housing, confirmed it runs to the outside, and re-tested — tissue held flat and the mirror cleared after a shower.

I agree on the record too: a note on the duct route and a before-and-after check is worth more than motor noise. What do you use to measure airflow on a small bath fan when the tissue test is borderline?
 